adiabatic equation - 2.5 2c SWA

I don't get involved with adiabatic equations all to often, hence I'm a bit rusty! I'm trying to calculate the R1+R2 for a 2 core 2.5mm SWA. Obviously the R1 is the easy bit, I'm struggling with the SWA as the R2.  I saw a link to a table on the old forum but I can't find it now. Any ideas?


Thanks Stewart
Parents
  • We are about 120 m away from the sub.


    The point I'm trying to make, is that without info from any of these posts on the fault level, the IET guidance for 100 A supplies is to assume 16 kA - and in fact where practicable the design is done for such installations in line with the 16 kA (and 0.35 external loop impedance) for dwellings to cover the fact that conditions may change. This is the bases of Section 7 of the OSG.
Reply
  • We are about 120 m away from the sub.


    The point I'm trying to make, is that without info from any of these posts on the fault level, the IET guidance for 100 A supplies is to assume 16 kA - and in fact where practicable the design is done for such installations in line with the 16 kA (and 0.35 external loop impedance) for dwellings to cover the fact that conditions may change. This is the bases of Section 7 of the OSG.