Chris Pearson:
Graham, now you are confusing me.
I can see the point of manufacturing gear to cope with 6, 10, 16 kVA on the basis that the installation may be literally next door to the transformer (so far I have resisted the temptation to knock on the door of our neighbour across the road with my MFT at the ready) but I am not sure why you mention the maximum (PME) external loop impedance.
The adiabatic tells me that 4 sqmm CPCs will suffice for all circuits given a Ze of 0.2 Ω - I cannot be more than 1150 A. If Ze is anywhere up to 0.35 Ω, the equation holds good.
However, I have assumed that Ze is 0.35 Ω when it comes to the ends of circuits because I need to be satisfied that Zs will be low enough to satisfy the requirements of ADS. If Ze is lower, the conditions are still met.
If I have that wrong, please let me know whilst I still have time to change the design.
Chris Pearson:
Graham, now you are confusing me.
I can see the point of manufacturing gear to cope with 6, 10, 16 kVA on the basis that the installation may be literally next door to the transformer (so far I have resisted the temptation to knock on the door of our neighbour across the road with my MFT at the ready) but I am not sure why you mention the maximum (PME) external loop impedance.
The adiabatic tells me that 4 sqmm CPCs will suffice for all circuits given a Ze of 0.2 Ω - I cannot be more than 1150 A. If Ze is anywhere up to 0.35 Ω, the equation holds good.
However, I have assumed that Ze is 0.35 Ω when it comes to the ends of circuits because I need to be satisfied that Zs will be low enough to satisfy the requirements of ADS. If Ze is lower, the conditions are still met.
If I have that wrong, please let me know whilst I still have time to change the design.