John Peckham:
The changes relating to this requirement were the move of the 40ms at 150mA from Chapter 41 to Part 6.
The big change I strongly object to is testing RCDs only at x5 or higher. The higher bit is just stupid! I have heard one manufacturer recommending a test at 250mA. What is the purpose of this test is it to get the RCD to trip? Or should it be a test the RCD at a potentially lethal current and verify it will disconnect the supply in a safe time.
Graham Kenyon posted a very good table on the old forum for testing of RCDS that I think should appear in the future AMD1 to the 18TH.
I note that the sad posts by Zoom of a double fatality concerning a shower and GB post of a fatality in rented premises could have been prevented by RCD protection.
John Peckham:
The changes relating to this requirement were the move of the 40ms at 150mA from Chapter 41 to Part 6.
The big change I strongly object to is testing RCDs only at x5 or higher. The higher bit is just stupid! I have heard one manufacturer recommending a test at 250mA. What is the purpose of this test is it to get the RCD to trip? Or should it be a test the RCD at a potentially lethal current and verify it will disconnect the supply in a safe time.
Graham Kenyon posted a very good table on the old forum for testing of RCDS that I think should appear in the future AMD1 to the 18TH.
I note that the sad posts by Zoom of a double fatality concerning a shower and GB post of a fatality in rented premises could have been prevented by RCD protection.