This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

RCD Testing x5 150mA (or higher for Hager RCCB)

Following on from John Peckham's recent post, I have recently installed several of Hager's consumer units with their new 100A 30mA Type A RCD (CD285U)


When testing the RCDs I noticed the trip times were much higher than previously experienced. Hager have said that RCCB needs to be tested at 250mA https://www.hager.co.uk/news-exhibitions-case-studies/18th-edition/updated-guidance-rccb-testing/97806.htm


In addition, if you have a Fluke you may notice that when carrying out a earth loop test (in no trip mode) the Fluke will fail to get a reading and trip the RCD. Apparently Hager have had a several reports of this and when I called could not explain it.
Parents
  • So a test current of 70mA at 230v then ( R= 230V / 3.3k ohms)

    as I said, neither 30mA nor  5 times it, just something to make it trip.

    Presumably those are marginal for use at 110V as well as 230V, although at 30mA test current would be only just about OK.

    Of course a good 30mA RCD fires at about 20-25mA so really it is fine.
Reply
  • So a test current of 70mA at 230v then ( R= 230V / 3.3k ohms)

    as I said, neither 30mA nor  5 times it, just something to make it trip.

    Presumably those are marginal for use at 110V as well as 230V, although at 30mA test current would be only just about OK.

    Of course a good 30mA RCD fires at about 20-25mA so really it is fine.
Children
No Data