Hi Graham,
I understand you wouldn't want to bond 2 separate installations together if they were running off of different tappings or different transformers etc, but if you had two installations (both PME converted to TT) in the area, both run from the same DNO cable, both 3 phase (or containing the same phase as the other), then bonding the two installations together would be acceptable, no? As long as the conductors can carry the maximum fault current likely to flow through them, as this would fit the requirements of 542.1.3.3?
I understand a TT electrode being an adequate distance away from exposed conductive metals connected to a PEN conductor, but if the services nearby are also converted to a TT, then this need not apply. Is this correct?
If I'm not understanding this properly, please correct me, every day is a school day after all!
SScho:
Hi Graham,
I understand you wouldn't want to bond 2 separate installations together if they were running off of different tappings or different transformers etc, but if you had two installations (both PME converted to TT) in the area, both run from the same DNO cable, both 3 phase (or containing the same phase as the other), then bonding the two installations together would be acceptable, no? As long as the conductors can carry the maximum fault current likely to flow through them, as this would fit the requirements of 542.1.3.3?
I understand a TT electrode being an adequate distance away from exposed conductive metals connected to a PEN conductor, but if the services nearby are also converted to a TT, then this need not apply. Is this correct?
If I'm not understanding this properly, please correct me, every day is a school day after all!