Andrew Jewsbury:
I've definitely seen RCDs with longer trip times at 5IΔn than at IΔn, so IΔn is not always the "worst case" either!
In which case, can we have any confidence that a 1x (or 5x) test will give realistic assurance that the RCD will open in the required time when subject to a real earth fault - which could be many amps in magnitude?
Most RCD testers do not test at 2IΔn, and therefore the only option is 5IΔn.
Cue for a new range of "18th Ed" RCD testers with a 2x option?
Perhaps more practically we should only be thinking in terms of 'sampling' the RCDs performance at a few points and if they're within spec then say it's reasonable to assume that the RCD is functioning as designed and so will operate within specification throughout its entire range. Perhaps single test (1x perhaps) would be sufficient. I gather that some manufacturers suggested that operating the T button and observing an 'immediate' trip could be sufficient.
These require RCDs for Additional Protection - in this case this would invoke the 5IΔn test. To add all these requirements together, we have a maximum loop impedance for a 30 mA RCD of 230*.95/0.15 Ω (where additional protection is needed), i.e. 1457 Ω and not 1667 Ω
Humm - not sure of the logic there - additional protection is usually aimed at situations of direct contact (nails through cables, flexes cut by lawnmowers, touching the contacts of lampholders) - where the c.p.c. and hence Zs aren't usually of relevance (likewise any calculations involving Uo or Cmin). In a functioning installation we're only really worried about 150mA going through the victim's body, where it goes after that isn't a concern. Certainly for a successful test we'd need a lowish loop impedance, but that requirement doesn't seem to be obviously written into BS 7671.
Would you think it acceptable to perform a 5x test by placing the tester's earth probe on the supply N rather than PE? That would avoid problems due to a high Zs but still test the RCD's fundamental operation?
If an RCD does not trip at 1 x Idelta n then it is defective. This softer test is a better indicator of RCD health than the 5 x test and consumer safety.
This does not unfortunately take account of a small number of cases where the RCD passes a 1x test, but then goes on to fail a 5x test, although I agree this is not simply a case of "sticky RCD".
In fact, I am undecided in some cases whether this phenomenon is a combination of other external influence and/or a property of how a particular test set operates under given conditions.
Having said that I have seen this behavior on devices with different test sets at the same time doesn't help, as an influence on the supply might well have caused the problem, and of course we know of cases where RCDs returned to manufacturers having "failed" on-site have been tested in isolation and found to be operating perfectly well.
But that in itself causes another question regarding RCDs used for Additional Protection, or fault protection where 0.2 s disconnection time is required ... i.e. will they actually operated as expected?
Graham Kenyon:
John,
In general, I don't really disagree with you, but ...If an RCD does not trip at 1 x Idelta n then it is defective. This softer test is a better indicator of RCD health than the 5 x test and consumer safety.
Chris Pearson:
Graham Kenyon:
John,
This does not unfortunately take account of a small number of cases where the RCD passes a 1x test, but then goes on to fail a 5x test, although I agree this is not simply a case of "sticky RCD".For my own peace of mind, at home, I would wish to be assured that an RCD does trip as intended. If passing at 5x means that one will also pass at 1x, then all well and good: only the one test is required. However, if not, then surely both tests are required.
Of course, there is no reason to stop doing the 5 tests, it is just that only one time needs to be recorded in the EIC/EICR (plus the all important test button).
| RCD Residual current Rating |
| Tests, results and notes |
| 10 mA |
| Conduct both 1x and 5x tests Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. |
| 30 mA |
| Conduct both 1x and 5x tests. Requires loop impedance less than 1364 Ω if you take into account full volt drop Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 1667 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated |
| 100 mA |
| Conduct both 1x and 5x tests. requires loop impedance less than 409 Ω if you take into account full volt drop Record the 5x result. Verifies ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 500 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated If you are asserting it's unsafe to test the RCD at 5x in domestic, then do and record the 1x, but now you only have verified disconnection at 1 s and compliance with 411.3.2.4, and therefore in domestic this RCD can only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2. |
| 300 mA |
| Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result. Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 300 mA RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
| 500 mA |
| Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 500 mA RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
| 100 mA Type S |
| Conduct both 1x and 5x tests. requires loop impedance less than 409 Ω if you take into account full volt drop Record the 5x result. Verifies ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. If you are asserting it's unsafe to test the RCD at 5x in domestic, then do and record the 1x, but now you only have verified disconnection at 1 s and compliance with 411.3.2.4, and therefore in domestic this RCD can only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
| 300 mA Type S |
| Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result. Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 300 mA Type S RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
| 500 mA Type S |
| Not practicable (or perhaps safe) to test at 5x, so we are limited here to testing at 1x. Record the 1x result. Verifies ADS to 643.7.1 b) for 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4, but not 411.3.2.1. This leads me to assert that the 500 mA Type S RCD may only provide ADS for distribution circuits, and final circuits not covered by 411.3.2.2 |
Graham Kenyon:
Chris Pearson:
Graham Kenyon:
John,
Of course, there is no reason to stop doing the 5 tests, it is just that only one time needs to be recorded in the EIC/EICR (plus the all important test button).I'm still not satisfied.
I think that I have been slightly mis-read here.
I was referring to the five tests at 1/2 Ideltan, Ideltan (x 2), and 5 Ideltan (x2). Performing them and writing them in a notebook is no bother at all.