30 mA |
Conduct both 1x and 5x tests. Requires loop impedance less than 1364 Ω if you take into account full volt drop Record the 5x result. Verifies both additional protection to 643.7 and ADS to 643.7.1 b) for 0.2 s and 1 s disconnection. I would be able to demonstrate compliance with Regulation 411.3.2.4 and 411.3.2.1. Whilst the full Zs of 1667 Ω presented in Table 41.5 wouldn't provide sufficient current for a 5x test with lower voltages, earth electrode resistance should be limited to 200 Ω so no issues anticipated |
Playing Devil's advocate for a moment... on a TT system is there a requirement to test a 30mA unit at 1x at all? While I can of course see the common sense in testing at 30mA, 643.8 seems only to actually require:
Also is there any value in using a lower multiple on a higher setting on the test instrument - e.g. using a 300mA x 1 as a better approximation to a 2x test for a 100mA device than a 5x 100mA test (and reduce the reliance on a low Zs in the process). Or is that instrument abuse?
On a different tangent, should we be verifying the RCD's reaction to d.c. components in the residual current too these days?
As for the test that produces a 220ms for a final circuit on a TT system requiring a 0.2s disconnection time that is for once clear in 643.7.1 as it says, " The effectiveness of the automatic disconnection of the supply by RCDs shall be verified using a suitable test equipment according to BS EN 61557-6 to confirm that the relevant requirements of Chapter 41 are met, taking account of the operating characteristics of the device". So a 220ms time would not meet the requirements of Chapter 41 although it would meet the product standard. The same would apply to RCDs to the older BS 4293 standard.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site