is not very tough so I wouldn't use it underground as per the You Tube video ZoomUp posted.
Tyre Company workshops wired in a black version of YY cable. Not so much innovation as cutting corners I think, as they basically wired the place in flex.
AJJewsbury:
is not very tough so I wouldn't use it underground as per the You Tube video ZoomUp posted.
Actually SWA isn't that touch either - it's easily pierced even by a simple garden fork never mind any kind of mechanical excavator - it's read advantage underground is from a surrounding c.p.c. that'll activate ADS rather than its physical toughness. In some ways, a copper rather than steel 'armour' might work better - which is actually what most modern buried DNO cables have.
Tyre Company workshops wired in a black version of YY cable. Not so much innovation as cutting corners I think, as they basically wired the place in flex.
I suspect it's more a cause of someone using continental contractors and them just doing what they usually do - German factories are routinely wired in YY etc (submains and all) - all according to their standards (which are normally held in reasonable regard). It begs the question: what's wrong with using "flex" for fixed wiring. We used to have a reg that prohibited it - but that dated from the day when "flexible cord" was a flimsy unsheathed composition of fine wires, cotton and rubber and nothing like as tough as the fixed wiring cables of the day - but these days when flex is plastic insulated and sheathed and so almost identical to many types of fixed wiring cable, other than the conductors are stranded. The reg has long since been deleted, but the memory of it seems to persist in folk memory for some reason. If anything using flex is normally more expensive (because of the extra work drawing many more strands and then twisting them together) - so it's hardly as cost cutting measure. It can however be quicker and easier to install and often makes better & more reliable connections in some common terminal types (or can be ferruled for screw tunnel terminals). So I'd make the case for considering it.
- Andy.
I ahem heard the argument before that you could -in theory- wire a house in flex, but would you do it?
I'm not sure about your comments that you can pierce a steel armoured cable as easily as a flexible SY etc.
Zoomup:
More E.V. charging safety concerns.
https://www.dailymail.co.uk/sciencetech/article-7086061/Electric-vehicle-drivers-UK-risking-death-electrocution-charging-car-home.html
Z.
mapj1:
Perhaps cars should come with a power of opportunity adapter kit containing a lead ending in two insulated croc clips, some thick gloves, a jemmy bar and a selection of keys for lamp posts and street boxes and so forth, and maybe some wire cutters. The ideal Christmas present for the intrepid EV owner. ?
There is a disconnection in the level of safety we expect for a traditional car where we happily use fuel pumps and jerry cans, when compared to the far higher level we expect for indoor electrics with ADS and all the rest.
mapj1:
Some of us are quite happy to specify and use SY and similar in situations where we think it is the best technical solution. It is important to realise that the braid is really best used as an EMC thing and not intended either as armour against attack by sharp objects nor are the fine strands good as a high current CPC. But for flexibility and shielding, ideal.
Equally there are those of us who consider BS7671 to be a guide, and not the last word in wiring standards, though I suspect to many others that is tantamount to heresy. However, I mainly work in a research environment, and as that is always pushing at non standard solutions, it probably colours my thinking somewhat.
AJJewsbury:
looking into supplying a client with an electric vehicle power supply from a three phase isolating transformer BS 7671 722.413 (1.2): " The circuit shall be supplied through a fixed isolating transformer.."
I'd take a step back and think carefully about that approach first. Isolating transformers can be used in a couple of different ways - either to provide a separated supply (i.e. no deliberate connection to earth as per section 413) or with one pole of the secondary deliberately earthed (to form a local TN system as per 411).
The trouble with the first approach is that many, if not most, electric cars check for a sound connection to earth (presumably a L-PE loop in practice) - and flatly refuse to charge if it's absent or has a high resistance. So a section 413 approach, although all very well and good and very safe in theory, probably isn't going to actually work in practice.
The other approach of turning the secondary into a TN system (normally TN-S) means you need to obtain an earth connection to connect the secondary to - in theory that could be the a local electrode or even the c.p.c. of the primary circuit. If it's a PME supply then using the primary circuit's c.p.c. is obviously out, which leaves a local electrode (and the need to keep the EVSE system out of reach of anything connected to the PME earth) - but if you're going for that you might as well just TT the EVSE and not bother with the expensive transformer at all.
There have been suggestions along the lines of and isolating transformer with the EVSE's PE conductor connected to the secondary "neutral" but without any kind of Earth connection - but that approach is completely outside of BS 7671 methods and has all kinds of potential risks that would need to be addresses (e.g. the secondary PE being capacitively coupled to the primary and so floating up to a hazardous voltage) and you wouldn't be able to describe the installation as complying with BS 7671.
- Andy.