RichardCS2:
Like many people here I have yet to see a convincing technical justification for a vehicle body being a higher risk thing to connect to a TNC-S derived earth than a metallic illuminated bus shelter. Especially the kind of bus shelter popular around here with metal seats incorporated into the design ensuring that its users spend an extended period of time with their backsides connected to the metalwork and their feet firmly on the ground. They are both similar sized objects made mostly of painted steel, they're both usually on poorly conducting surfaces, what's special about the car? Or are both dangerous and bus shelter electrical installations should really be class 2 as telephone box lighting is/was? Perhaps the car manufacturer's are fundamentally at fault making the cars class 1 in the first place, after all other outdoor appliances have long been class 2.
As a side note high-power AC charging seems to be dying, the main model to support it was the Renault Zoe and they have recently announced that future models will be restricted to 32 A per phase but 100 kW DC charging will be introduced in its place.
https://insideevs.com/news/342860/renault-ends-sale-of-zoe-q90-with-43-kw-ac-charging-capability/
Provided there's no connection to Earth (with capital E), or a protective conductor of another circuit, this should meet 413.
The use of a safety isolating transformer to provide an isolated supply seems to be being criticised here as unsafe in some way. An isolating transformer construction prevents any significant secondary voltage to any part of the primary circuit by class 2 insulation and an earthed screen between windings, so I cannot understand Andy's comment about capacitive coupling.
AJJewsbury:
Provided there's no connection to Earth (with capital E), or a protective conductor of another circuit, this should meet 413.
I can't see how connecting the EVSE's PE to a separated live conductor complies with section 413 at all. 413.3.3 demands that live parts of the separated circuit are not connected at any point to another circuit or to Earth or to a protective conductor - as I read it that's any protective conductor, not just protective conductors of other circuits.
Graham's wording seem to align more with 418.3.4 than 413 (which in a way would make more sense for a situation where we have multiple items of class I equipment on the same separated circuit) but the whole of section 418 is out of bounds for situations not overseen by skilled or instructed persons - so that's not really a goer either.
How is it a protective conductor if it's not used for ADS because the means of protection against electric shock is Electrical Separation? (See definition of Protective Conductor in Part 2 - specifically, it's definitely not "PE" in this instance, more "FE".)
gkenyon:
The situation that does arise, however, is high inrush current of the rather sizeable transformers. Yes, this can be overcome, but of course costs are now increasing, and we're competing against "forget it, I'll just plug it in to a socket-outlet", which of course is far less practical, and far less safe, but doesn't have the price tag attached.
gkenyon:
The answer is relatively simple, and lies in Table 6.2.15 of G12/4 (page 32) - it's to do with the load, and the required consumer earth electrode to help prevent earth potential rise in the event of a broken CNE conductor in the PME distrubution system. Additionally, the structure of the shelter may be able to act as a form of earth electrode depending on construction.