Earthing and the radio amateur
I've recently joined the IET forums. I replied to a  topic regarding amateur radio and PME on the old forum. Unfortunately I cant access the old forum anymore so I thought it would be best to start a new topic.
So. On the bench there is a transceiver with a metal case. Next to the transceiver there is a antenna tuning unit which is connected to a antenna system which is using an earth rod. Am I right in saying there is a chance of a potential difference between the two metal cases of the equipment regardless if it is a TT, TNS or TNCS?
What would be the ideal solution?  Put the shack on it's own TT supply and bond all the radio equipment back to the MET of the TT and if a earth rod is used for the antennas connect that back to the MET also?
If the TT system was not an option what would be best if the supply was a PME and you didn't want to use balanced antennas removing the use of an earth rod?
To be honest I've never really given PME's and amateur radio much thought which in hindsight was probably a mistake. I do remember when I did my training an earth rod was recommended for the radios.
Apologies for being so random.
Stewart M0SDM
  • Thanks for all those that have replied. It is all very interesting. It's clear to see there are lots of different opinions on the subject. I have read the RSGB leaflet.
    If you were going to right a list of do's and don'ts regarding earthing for the radio amateur what would it contain?
  • In reply to David Stone I have this to say. I was initially considering an external outbuilding as a radio shack. I have seen several garden sheds or old wash houses used as an amateur radio enthusiast's radio room. Ships' radio rooms may have confused me not being called shacks.  Now I understand that a radio shack can be an internal room in a house.
    The items mentioned like radiators, storage radiators or metal pipes may or may not be extraneous-conductive-parts within a house. It depends on how well they are connected to earth. If plastic pipes are used a central heating radiator may not be connected  with earth at all, or very poorly. An electric storage heater will be earthed via its circuit protective conductor, but if the house is TT earthed then that is not a problem. So many new properties are supplied by plastic main pipes these days, such as gas and water so no main equipotential bonding within the house will be required.
    A whole house can easily be converted to TT earthing from PME earthing if required. That would just need the PME earth conductor disconnecting and a separate earth electrode installed in a suitable location and connected to the house main earthing terminal. RCD protection then is essential on all circuits.
    With PME earthing that is why electricians are required to install 10mm2 main-equipotential-bonding
    conductors to extraneous-conductive-parts in a house and other locations, to mitigate potential shock risks in case of a lost neutral on the incoming supply cable. And that does happen as has been reported on the IET electrician's forum.
    I know little about amateur radio so am just speaking from the point of view of an electrician and BS 7671.
    C.
  • Thank you for your reply Clive.
    As I attempted to make clear, this is not a simple problem, and needs considerable background on more than the basics in BS7671. At the present time we do appear to have a problem with our mains supplies, and the reliability of neutral integrity. It is wise to consider all domestic supplies to be TNC-S unless TT is definitely installed, and reasonably isolated from surrounding properties by distance. I find from teaching the 18th edition update courses that many electricians have quite a knowledge gap around TT as a concept, unless they normally work outside of towns. Whatever the situation I would strongly advise against trying to TT one space in an otherwise TNC-S property as the chance of bringing an appliance connected to the other earthing system into the wrong space is considerable because any fault on the TN system will produce a dangerous potential between the appliances on differing earthing systems.
    David CEng MIET G8FNR
  • David Stone:
    The more I read about PME failure it makes me think we would be better off without it.
  • Yes Stewart,
                             I was once called to a mid 70s neighbour's house where electrical items were not working correctly. I measured 240 Volts L to E and L to N. The supply was an underground TN-C-S. Eventually I twigged that when heavy loads were turned on the supply Voltage dropped considerably, and I suspected a bad N joint in the road. Jointers arrived and the joint was found. Indeed the fault was due to a corroded connection on an aluminium cable. I talked to the jointers and was told that this happened on a regular basis with old underground aluminium joints. The aluminium is compressed with a crimp joint but loses its strength and then allows the joint to become loose. Then I squared R heating takes place and the situation gets worse.
    I would happily export a TNCS earth to a remote shed as long as all metalwork was bonded or earthed as appropriate.
    The radio equipment will perhaps run off DC via an internal AC/DC transformer to reduce the voltage and bridge rectifier to change the AC to DC so i would expect an earth fault path from the AC system is perhaps impossible until you attach your home made lighting rod radio aerial to the MET.
    I would be tempted not to bond the aerial at all as that might introduce a shock risk that would otherwise not be there and could introduce interference from DNO network currents flowing through the aerial to the MET but would of course bow down to greater knowledge.
  • As a radio amateur I'm interested in this discussion as I have the same situation as Stewart.
    As has been suggested, there are ways to mitigate the risk of electric shock in the shack without bonding the antenna ground rod to the MET, but is there an issue with lightning protection? It has been suggested to me that a nearby strike could induce a voltage gradient in the surrounding ground that might cause arcing into the property. Would bonding reduce this risk?
    Mike G8GYW
  • Purely from an electrician's point of view, a P.M.E. supply to a radio shack that has earthed equipment with conductive parts such as earthed cases that can be touched can present shock risks. The P.M.E. earth is connected directly to the neutral of the supply cable at the main intake meter position in the house. The neutral can attain a Voltage above true earth, as the neutral carries current and supply conductor cables' resistance cause a Voltage rise on the neutral. So, a P.M.E. earth terminal in the house can attain a Voltage above true earth, and this Voltage can appear on earthed equipment in the radio shack.
    If you have conductive parts in the shack that are earthed via an earth rod at the shack, there can be a Voltage appearing between TT earthed equipment and P.M.E. earthed equipment. This is undesirable, and could be dangerous.
    Although PME is often held up as a worst case example - there are similar dangers from having any two unconnected earthing systems within reach of each other - regardless of which type they are.
    With any TN system a fault between a line conductor and true earth (but not a c.p.c) can result in the star point being pulled a long way from zero volts - which is then imposed on the DNO's earth equally in TN-S and TN-C-S systems.
    Likewise standing leakage currents in a TT installation can raise the MET and everything connected to it significantly above zero volts - no more than 50V if the installation is in accordance with BS 7671 and all RCDs are functioning correctly, but another TT installation could be at held at a different voltage again. In the worst case if the other installation is on another phase, you could have as much as 50V √3 = about 87V between them.
    Then there are a whole raft of faults (L-PE on any TN system, plus L-N on TN-C-S systems) that can temporarily raise the voltage on earthed conductors - most installation ones should clear within 5s, but DNO ones could take longer.
    In short, try not to have any two different earthing systems within reach of each other, whether one of them is PME or not.
  • The problem is that the radio ham, by putting bits of wire and metal outdoors, more often than not has more than one earthing system. Maybe not if if the station is VHF/UHF only and the antennas are all yagi designs looking like an overgrown TV antenna on the roof, as these do not need an RF earth to function, but a station for HF or even more so LF, is not really complete without a decent connection to the  earth beneath the antenna.
    So given you have an earthed extraneous part to deal with, the options are somewhat restricted.
    As far as lightning is concerned, any outdoor tower or mast, if not planted directly in the ground, should be arranged so that it can flash over  to an electrode if it is more than a few hundred volts off true earth.  A simple spark gap will do. Similar precautions to protect  external feed cables before they go indoors are also advised.
    Sealed unit spark gaps with an inert gas filling are available. examples  though the breakdown voltages are a bit low for full legal power operation.
      For a direct strike, like the rest of the installation, such measures will of course be blown to smithereens, but for the far more likely induced few tens of KV from a strike within a km or so, they do greatly increase the chances of the indoor gear surviving, and of not injecting nasty voltages onto the local mains supply.
    Gas discharge tubes and spark gaps allow a short to ground to be present only when it is actually needed, being open circuit the rest of the time! Howeverby far the best precaution to protect the house end is to disconnect the radio, from both antenna and mains supply, when not in use, and to short the antennas to ground if their design allows that.
  • Thanks for that.
    In my case, the antenna is an HF end fed half wave wire, connected to the transceiver via a voltage transformer and coax. Due to the constraints of our property it is only 12 feet above ground.
    The ground rod is connected to the coax shield and is there to prevent static build up. It is not an RF ground (that function is provided by a section of the coax feeder which acts as a counterpoise).
    When not in use I disconnect the antenna from the transceiver and its power supply from the mains. I'd like to know if any further precautions against lightning strikes are required. We haven't had one in this area for forty years, but you never know ...