BS 3871 Miniature Circuit Breakers Let Through Energy

Currently involved in a project where I need to do the energy let through calculations for existing circuit breakers to prove that the increased fault current even though within the breaking capacity of the MCB, damage will not occur to the final circuit cables.


In a nutshell, the following formula must be true I2t<k2S2 . In BS 60898 MCBs the I2t is provided by the manufacturers as these are energy limiting devices.


As these happen to be BS 3871 and in the absence of such data can I get your recommendations? Use a definite trip time of 10ms and plug that in the equation?


Thanks

Mike
Parents
  • I am surprised DS cannot rustle up a data sheet for the load limiter 9kA   those are the modern ones, just before the new standard came out.
Reply
  • I am surprised DS cannot rustle up a data sheet for the load limiter 9kA   those are the modern ones, just before the new standard came out.