apologies if you are already aware of this but with respect to the x5 or greater test current introduced in the 18th, Hager have advised that their RCBO units are manufactured to the 2017 amended version of BSEN61008/9 which permitted disconnection within 40ms at 250mA. Thus they advise testing at x 5 on both sides with the instrument set for 50mA on the variable range.
The Megger 1471 tester has a setting "VAR" where you can add compensation to the test to apply the desired setting.
Also not sure if I have read mike's comment correctly regarding simplification of regs but neither test have been removed. You have to use the correct time setting depending on what you are using the RCD for i.e. fault or additional protection and received rs this result.
The Megger 1471 tester has a setting "VAR" where you can add compensation to the test to apply the desired setting.
Also not sure if I have read mike's comment correctly regarding simplification of regs but neither test have been removed. You have to use the correct time setting depending on what you are using the RCD for i.e. fault or additional protection and received rs this result.