643.8 Additional protection
The verification of the effectiveness of the measures applied for additional protection is fulfilled by visual inspection
and testing. Where RCDs are required for additional protection, the effectiveness of automatic disconnection of
supply by RCDs shall be verified using suitable test equipment according to BS EN 61557-6 (see Regulation
643 .I) to confirm that the relevant requirements of Chapter 41 are met.
NOTE: Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1
disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating
current
My bold in the italics - now to me, and maybe to others, this says 'it is OK not to bother to check at the 30mA rating' Anything more than 5 times that would count as a pass, in principle even a test at many amps. ' That is an implication that I do not like.
That's correct. 5x for additional protection and 1x for fault protection
MS2000:
The Megger 1471 tester has a setting "VAR" where you can add compensation to the test to apply the desired setting.
Also not sure if I have read mike's comment correctly regarding simplification of regs but neither test have been removed. You have to use the correct time setting depending on what you are using the RCD for i.e. fault or additional protection and received rs this result.