This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

RCD x 5

apologies if you are already aware of this but with respect to the x5 or greater test current introduced in the 18th, Hager have advised that their RCBO units are manufactured to the 2017 amended version of BSEN61008/9 which permitted disconnection within 40ms at 250mA. Thus they advise testing at x 5 on both sides with the instrument set for 50mA on the variable range.
Parents
  • Former Community Member
    0 Former Community Member
    That's correct. 5x for additional protection and 1x for fault protection
Reply
  • Former Community Member
    0 Former Community Member
    That's correct. 5x for additional protection and 1x for fault protection
Children
No Data