RCD x 5

apologies if you are already aware of this but with respect to the x5 or greater test current introduced in the 18th, Hager have advised that their RCBO units are manufactured to the 2017 amended version of BSEN61008/9 which permitted disconnection within 40ms at 250mA. Thus they advise testing at x 5 on both sides with the instrument set for 50mA on the variable range.
Parents
  • The cynic in me wonders if lobbying took place because somewhere there was a warehouse bulging with not quite compliant RCD mechanisms waiting for a rule change to allow them to be unloaded on the unsuspecting muggins. There is some precedent for this in other industries.
Reply
  • The cynic in me wonders if lobbying took place because somewhere there was a warehouse bulging with not quite compliant RCD mechanisms waiting for a rule change to allow them to be unloaded on the unsuspecting muggins. There is some precedent for this in other industries.