Diesel Generator Fault Levels

Hello all,


I am looking to specify a temporary mobile diesel generator and as such looking into the disconnection times and the maximum fault current provided by the genset.

I have contacted a provider and got the specification of the alternator in their genset, images below of the fault current graph and the alternator per unit values.


I am looking into understanding what values to use. Am I correct in getting the sustained fault level and for an earth fault to apply the multiplication factor of 2.5 for sustained? I will make sure my disconnection times are less than the sustained maximum duration in order to not trip the generator breaker and loose all of the supply.


Alternator is 50Hz 415V

fc5681c638e7bada3947e466b96400fd-huge-newage-hci534e_1.jpg

3106a5e7994134e881a5487cbbe73194-huge-newage-hci534e.jpg


Parents
  • Thanks Dave and perspicacious, your responses seem reasonable to be honest, the table with the fault multipliers though has a time limit per fault type and for that I assumed that the time durations and levels corresponded to the alternator actually been driven by that diesel engine.


    Thanks

    Mike
Reply
  • Thanks Dave and perspicacious, your responses seem reasonable to be honest, the table with the fault multipliers though has a time limit per fault type and for that I assumed that the time durations and levels corresponded to the alternator actually been driven by that diesel engine.


    Thanks

    Mike