Hello all,


I am looking to specify a temporary mobile diesel generator and as such looking into the disconnection times and the maximum fault current provided by the genset.

I have contacted a provider and got the specification of the alternator in their genset, images below of the fault current graph and the alternator per unit values.


I am looking into understanding what values to use. Am I correct in getting the sustained fault level and for an earth fault to apply the multiplication factor of 2.5 for sustained? I will make sure my disconnection times are less than the sustained maximum duration in order to not trip the generator breaker and loose all of the supply.


Alternator is 50Hz 415V

fc5681c638e7bada3947e466b96400fd-huge-newage-hci534e_1.jpg

3106a5e7994134e881a5487cbbe73194-huge-newage-hci534e.jpg


Parents
  • If you are looking at setting the Vigis to 0.4 second delay on over current,  you have to ask why - there is no need for fast disconnections  on  L-N and LL faults, you may as well let the lower tier of breakers pick up if it can. this can be set to up to 5 seconds if you fancy, though 1 is probably enough, but set the In multiplier low, less than 2000A

    LE faults will be picked up by the I delta N function, which can be set to quite a high value - a few amps, to allow any lower tier faults to be picked up by local RCDs where fitted, but obviously a shorter delay, perhaps 250-300msec.

    I have no idea what number Amtech is expecting, though I fear the authors were not really aware of the full subtlety of genset supplies.


    By all means use the software, but be aware that you may need to do the sums twice, once with a high value for all the fast breakers, and again with a much lower value for the slower ones, and being a bit grey of hair, I'd recommend to do some sanity check estimates the old way to make sure it is not miles out for some reason.



    In general an LLL fault is about twice the LN fault current, and the effect of an asymmetric transient  (phase varying when in the cycle the fault comes on )is also about 2:1 at the start, but settles after the first couple of cycles.
Reply
  • If you are looking at setting the Vigis to 0.4 second delay on over current,  you have to ask why - there is no need for fast disconnections  on  L-N and LL faults, you may as well let the lower tier of breakers pick up if it can. this can be set to up to 5 seconds if you fancy, though 1 is probably enough, but set the In multiplier low, less than 2000A

    LE faults will be picked up by the I delta N function, which can be set to quite a high value - a few amps, to allow any lower tier faults to be picked up by local RCDs where fitted, but obviously a shorter delay, perhaps 250-300msec.

    I have no idea what number Amtech is expecting, though I fear the authors were not really aware of the full subtlety of genset supplies.


    By all means use the software, but be aware that you may need to do the sums twice, once with a high value for all the fast breakers, and again with a much lower value for the slower ones, and being a bit grey of hair, I'd recommend to do some sanity check estimates the old way to make sure it is not miles out for some reason.



    In general an LLL fault is about twice the LN fault current, and the effect of an asymmetric transient  (phase varying when in the cycle the fault comes on )is also about 2:1 at the start, but settles after the first couple of cycles.