AFDD Installation - TPN Board

Former Community Member
Former Community Member
Has anyone installed AFDDs on a three phase board?

I'm looking at installing a DIN rail board underneath the TPN DB with a cable way in between and mounting the AFDDs within the DIN rail box,

Has anyone else installed them in this way?


Thanks
Parents
  • I spoke to Wylex earlier this year,  the double pole RCBOs that are compatible with the arc fault devices cannot be used in a three phase board as they do not have phase barriers.


    Andy B
Reply
  • I spoke to Wylex earlier this year,  the double pole RCBOs that are compatible with the arc fault devices cannot be used in a three phase board as they do not have phase barriers.


    Andy B