Dodgy garage installation - borrowed neutrals?

This photo appeared in a car advert which was mentioned in a motoring forum.


The three lines all appear to make their way to the 3-phase board, but I cannot quite see why is happening to the neutrals.


Presumably the meter fitters were content that all was in order, although I suppose that the supplier's' principal concern is billing.


Would nobody give it a satisfactory EICR?

fe04cba68d8023216b9d65ea7caac269-huge-8a324a46-e898-499a-9e06-beead3f8b6bf.jpg

Parents
  • I agree with Mike - 'looping' N though two or more meters doesn't affect the measurements - and was commonly seen in olden days when 3-phase supplies were metered using three separate single phase meters.


    So not borrowed N, just a common N for a single 3 phase circuit.


    Curiously, BS 7671 wouldn't have an issue with it anyway even if it was borrowed and not on the supplier's side, as (for reasons I've still yet to fathom) 314.4 only applies to final circuits.


       - Andy.
Reply
  • I agree with Mike - 'looping' N though two or more meters doesn't affect the measurements - and was commonly seen in olden days when 3-phase supplies were metered using three separate single phase meters.


    So not borrowed N, just a common N for a single 3 phase circuit.


    Curiously, BS 7671 wouldn't have an issue with it anyway even if it was borrowed and not on the supplier's side, as (for reasons I've still yet to fathom) 314.4 only applies to final circuits.