Any switch controlling a 13 Amp socket must be able to carry at least 13 Amps. That is what the 13 Amp socket can supply. A grid switch rated at 16 or 20 Amps could be used.
Z.If the socket has a BS 1363 plug fitted with a BS 1362 fuse rated 13A then it could be supplying 20 for a significant period (>3hours). Take a look at the fuse characteristics
.
Alasdair Anderson:
Zoomup:
Any switch controlling a 13 Amp socket must be able to carry at least 13 Amps. That is what the 13 Amp socket can supply. A grid switch rated at 16 or 20 Amps could be used.
Z.If the socket has a BS 1363 plug fitted with a BS 1362 fuse rated 13A then it could be supplying 20 for a significant period (>3hours). Take a look at the fuse characteristics
.