AJJewsbury:
Presumably the single 13 Amp sockets are behind the appliances like the fridge freezer, or at high level above the extractor hood, so are very unlikely to be used for additional appliances. That is why there are conveniently positioned grid control switches. Therefore this is a non-issue. A 10 Amp grid switch will not catch fire or blow up if carrying 11 Amps in most cases. A 20 Amp grid switch will be fine for other appliances like washing machines or tumble driers etc. Overloading is very unlikely if the single 13 Amp sockets are inaccessible. Stop worrying needlessly.
Ah, but you're only considering overload - what about fault currents?
- Andy.
AJJewsbury:
Presumably the single 13 Amp sockets are behind the appliances like the fridge freezer, or at high level above the extractor hood, so are very unlikely to be used for additional appliances. That is why there are conveniently positioned grid control switches. Therefore this is a non-issue. A 10 Amp grid switch will not catch fire or blow up if carrying 11 Amps in most cases. A 20 Amp grid switch will be fine for other appliances like washing machines or tumble driers etc. Overloading is very unlikely if the single 13 Amp sockets are inaccessible. Stop worrying needlessly.
Ah, but you're only considering overload - what about fault currents?
- Andy.