Chris Pearson:
gkenyon:
This leads to the question "Is it OK for a tumble dryer and a washing machine to be simultaneously plugged into a double socket-outlet?"
Answers on a postcard to ...Ours have been for the past 20-odd years. ?
Of course, it depends upon the machines. Ours total 5.15 kW = 22 A, which exceeds a double socket's rating of 20 A until diversity comes into play.
Chris Pearson:
gkenyon:
This leads to the question "Is it OK for a tumble dryer and a washing machine to be simultaneously plugged into a double socket-outlet?"
Answers on a postcard to ...Ours have been for the past 20-odd years. ?
Of course, it depends upon the machines. Ours total 5.15 kW = 22 A, which exceeds a double socket's rating of 20 A until diversity comes into play.