Chris Pearson:
BS1363-2:2016+A1:2018
<snip>
Section 6: classification and rating
6.1 The rated current of all socket-outlets shall be 13 A
<snip>
Section 16 specifies 14 A + 6 A for temperature testing.
It must be that every BS1363 socket can safely supply 13 A indefinitely because that is what users are entitled to expect of them. Nowhere does it say that the total of a multiple socket-outlet is limited to 13 A. It is not expressly stated, but if a twin socket-outlet may safely supply 14 A + 6 A for at least 4 hours with a stable temperature, it may be inferred that it is safe to do so.
Chris Pearson:
BS1363-2:2016+A1:2018
<snip>
Section 6: classification and rating
6.1 The rated current of all socket-outlets shall be 13 A
<snip>
Section 16 specifies 14 A + 6 A for temperature testing.
It must be that every BS1363 socket can safely supply 13 A indefinitely because that is what users are entitled to expect of them. Nowhere does it say that the total of a multiple socket-outlet is limited to 13 A. It is not expressly stated, but if a twin socket-outlet may safely supply 14 A + 6 A for at least 4 hours with a stable temperature, it may be inferred that it is safe to do so.