TNCS 6mm main earth - EICR

Just wondering what peoples first thoughts are on a 6mm main earth. 0.27ze, TNCS. 80A 1361 main fuse.


Iv'e tried doing a search on here but it did not come up with any results. (Maybe user error!). I'm sure this subject would have come up before.


Thanks
Parents
  • 850A is very quick if you take the right 1361 curves. In general at a ballpark rule of thumb for anything simple and hot wire based, at 10 times the normal 'no break' rating,

    you pass the 0.4 secs required for TN isolation. we are well over 600A, and speed goes as the square of current in this region. even with 3036  the rule of thumb is only a factor of 2 away.
    53e1d3ae6392a6d5354c10a740e5b72d-huge-bs1361_curves_850a.gif


    conclusion, if it was only blowing the fuse we worried about, 6mm will be fine.
Reply
  • 850A is very quick if you take the right 1361 curves. In general at a ballpark rule of thumb for anything simple and hot wire based, at 10 times the normal 'no break' rating,

    you pass the 0.4 secs required for TN isolation. we are well over 600A, and speed goes as the square of current in this region. even with 3036  the rule of thumb is only a factor of 2 away.
    53e1d3ae6392a6d5354c10a740e5b72d-huge-bs1361_curves_850a.gif


    conclusion, if it was only blowing the fuse we worried about, 6mm will be fine.