I would use 3no Quadrafoil Groups - you don't say what ampacity you want but for up to say 2.0MVA the quadrafoil would be easiest for you
Google that and look for Ellis Patents cable cleats
For each of the 3 groups try and contra rotate the phase conductors - each group of 4 contains L1, L2, L3 and N
Regards
OMS
So there is no problem with having a neutral on the outside of the last group? The reason for the question is IET GN 6 implies the neutrals should only be installed between groups. Therefore, this would only allow two neutrals for three groups, if you follow?
I would use 3no Quadrafoil Groups - you don't say what ampacity you want but for up to say 2.0MVA the quadrafoil would be easiest for you
Google that and look for Ellis Patents cable cleats
For each of the 3 groups try and contra rotate the phase conductors - each group of 4 contains L1, L2, L3 and N
Regards
OMS
So there is no problem with having a neutral on the outside of the last group? The reason for the question is IET GN 6 implies the neutrals should only be installed between groups. Therefore, this would only allow two neutrals for three groups, if you follow?