mapj1:
If the extraneous-conductive-part is bonded to one installation already, and you then bond it again to another installation, the second protective conductor [main protective bonding conductor] surely becomes common to both installations.
But the idea that they are not bonded is something of a mistake, reliable isolation cannot be acheived, adjacent buildings share gas and water pipes accross multiple methods of earthing (TT and PME is commonly mixed on farms, where the house is PME, and the farm proper is very much TT. Both have water. Mixed TNC-s and TNs on the same substation is common in built up areas with mixed ages of property), not to mention water and gas pipes also interlinking the CPCs of multiple substations.
perhaps we need to permit fuses and breakers in the CPC after all ?
mapj1:
If the extraneous-conductive-part is bonded to one installation already, and you then bond it again to another installation, the second protective conductor [main protective bonding conductor] surely becomes common to both installations.
But the idea that they are not bonded is something of a mistake, reliable isolation cannot be acheived, adjacent buildings share gas and water pipes accross multiple methods of earthing (TT and PME is commonly mixed on farms, where the house is PME, and the farm proper is very much TT. Both have water. Mixed TNC-s and TNs on the same substation is common in built up areas with mixed ages of property), not to mention water and gas pipes also interlinking the CPCs of multiple substations.
perhaps we need to permit fuses and breakers in the CPC after all ?