SScho:
Good afternoon all,
I'm part of one of the teams installing the EV charging points around London and we keep running into the same situations and problems when going through the site selection process - proximity of other electrified street furniture to the units we are installing (as well as potentially plugged in cars which is measured to the edge of the parking bay.)
Regs say that any EV installation cannot be connected to a PME system and must be converted to a TT in case of a damaged/faulty PEN conductor. Naturally if you're converting something to a TT system and not using the DNO TN-C-S earthing arrangement, there must be a reasonable distance between the TT and any other TN-C or TN-C-S systems (2m or so is reasonable).
If there were other services in the vicinity but can be proven that these have also been converted to TT and are 100% confirmed to not be using the DNO earth, would it be reasonable to say that the requirement for the 2m distance can be reduced or ignored completely?
411.3.1.1 Protective earthing
Exposed-conductive-parts shall be connected to a protective conductor under the specific conditions for each type of system earthing as specified in Regulations 411.4 to 411.6.
Simultaneously accessible exposed-conductive-parts shall be connected to the same earthing system individually, in groups or collectively.
...
Another thought I've had is to bond the cabinets together - being on the same type of system, it makes logical sense that this would in turn reduce the Ze and improve disconnection times, both units have their methods of ADS and incorporate an RCD/RCBO of a 61008 or 61009 standard respectively.
Any other thoughts or ideas would be much appreciated as I try and figure a workaround for this issue. I understand this could work for smaller cabinets and for individual supplies, and not necessarily for street lighting which might not be adequately equipped for being converted to TT (bit of a bigger job to start installing RCDs and then giving a minor works cert etc.).
Well, isolating transformer is one option
AJJewsbury:
Well, isolating transformer is one option
How would that work? You can't use it to create a separated system as most EVs check for an earth connection before commencing charge. If you attempt to create your own local TN (or TT) system then you need a source earth electrode - so back to square 1.
The only other option I can think of is a floating system with PE connected to N (but not earth) - but as far as I know BS 7671 doesn't recognise such arrangements - which makes it quite a limb to go out on.
- Andy.
SScho:
I'm part of one of the teams installing the EV charging points around London and we keep running into the same situations and problems when going through the site selection process - proximity of other electrified street furniture to the units we are installing (as well as potentially plugged in cars which is measured to the edge of the parking bay.)
SScho:
Good afternoon all,
I'm part of one of the teams installing the EV charging points around London and we keep running into the same situations and problems when going through the site selection process - proximity of other electrified street furniture to the units we are installing (as well as potentially plugged in cars which is measured to the edge of the parking bay.)
Regs say that any EV installation cannot be connected to a PME system and must be converted to a TT in case of a damaged/faulty PEN conductor. Naturally if you're converting something to a TT system and not using the DNO TN-C-S earthing arrangement, there must be a reasonable distance between the TT and any other TN-C or TN-C-S systems (2m or so is reasonable).
If there were other services in the vicinity but can be proven that these have also been converted to TT and are 100% confirmed to not be using the DNO earth, would it be reasonable to say that the requirement for the 2m distance can be reduced or ignored completely? Another thought I've had is to bond the cabinets together - being on the same type of system, it makes logical sense that this would in turn reduce the Ze and improve disconnection times, both units have their methods of ADS and incorporate an RCD/RCBO of a 61008 or 61009 standard respectively.
Any other thoughts or ideas would be much appreciated as I try and figure a workaround for this issue. I understand this could work for smaller cabinets and for individual supplies, and not necessarily for street lighting which might not be adequately equipped for being converted to TT (bit of a bigger job to start installing RCDs and then giving a minor works cert etc.).
That initially sounds like a good suggestion, and if both TT, might have addressed the 411.3.1.1 requirement. BUT, there are a couple of other considerations. For example, if they are not connected to the same supply transformer, or any of the TT earth electrodes are too close to PME buried earth (or worse, HV!) then you might have an issue with impulses and fault transfer potential.
Which is why there is another fundamental requirement of BS 7671 - 542.1.3.3, which says you need to be very, very careful bonding earths of different installations together, and you take full responsibility for that.
I appreciate that increasing numbers of EV points, or even non-electrified street furniture, mean that the available spaces are disappearing, but what has been done to date? How have you coped so far?
It's incredibly difficult and we are trying to find an electrical solution which reduces or negates the need to be a certain distance from other installations or street furniture, we also have to comply with many other factors as well, such as noise pollution to the adjacent properties, light intrusion if there are windows next to where we want to put them, if there's any underground structures we can't dig through... the list goes on! There's actually a pretty good document which outlines the requirements of EV charging points - http://ukevse.org.uk/resources/procurement-guidance/
Are you responsible for the design or the install only?
I can see the earthing of EVC points being a major headache in a cramped city centre with existing street lighting, CCTV, ANPR, comms cabinets and so on.
I've never been involved in EVC. I was talking to an estates manager this morning that has been instructed to arrange for 500kW of EVC to be installed at their site.
Time for some CPD.
Regards
Parsley
I essentially am part of the install only as the client provides their own charge points which are all pre-built and shipped over, but I'm sure if we can come to an agreement or a redesign then this could change. We install mainly 7kW and 22kW charge points.
500kW of EVC's Is one hell of a lot. I know Tesla have unveiled a 250kW charge point which requires a 1MW transformer to power 4 of them but we simply don't have the infrastructure to cope with that at the moment. I was asked to look at an install elsewhere as someone wanted to know how many 50kW rapid chargers would fit in the car park - long story short, they didn't go with it as it required a new HV supply to a brand new substation for a few charge points which would have been too powerful for the nature of the car park. (you wouldn't really have a 50kW in a "Park & Ride" as chances are you're going to be a good few hours!), if you need any help with this then I'll be happy to lend some assistance where I can.