Parsley:
Unfortunately separating HV and LV earthing systems on many existing sites isn't practicable.
mapj1:However, I suspect that there won't be many 2m long insulating joints available for upgrading gas and water mains to current standards to permit TT and PME to co-exist, and I think that the idea that the earthing systems can always be separated in this way remains very optimistic.
Parsley:
Unfortunately separating HV and LV earthing systems on many existing sites isn't practicable.
mapj1:However, I suspect that there won't be many 2m long insulating joints available for upgrading gas and water mains to current standards to permit TT and PME to co-exist, and I think that the idea that the earthing systems can always be separated in this way remains very optimistic.