gkenyon:
The issue we are discussing here is a little different - that of a TT supply separated from the network (specifically, the PME system). However, there are situations for EV charging installations where physical separation above and below ground cannot be achieved also.mapj1:However, I suspect that there won't be many 2m long insulating joints available for upgrading gas and water mains to current standards to permit TT and PME to co-exist, and I think that the idea that the earthing systems can always be separated in this way remains very optimistic.
I've seen one DNO that requires 3.5 m separation. Above ground at least, arm's reach (2.5 m) would be required by BS 7671.
My understanding is that metal gas and water mains, at least in the street, are being (or have been) replaced by plastic. Once this is completed, the place any remaining pipework (the bit up the driveway of a house, for example) is connected to the PME earthing system is in consumer's premises.
The situation may well be muddied by supply cables which have a conductive (or effectively conductive) earthed outer sheath.
But would it mean I can convert a whole installation to TT? Not always simple if an adjoining property is on PME. There are a number of situations where you might get caught out, e.g. two properties have roof-mounted TV antennas - the antenna systems may [should, but I know they aren't always] be earthed at one point, so if they are in arm's reach (or 3.5 m in one case) ...
"Providing a dedicated TT earthing system is only acceptable if there is no possibility of simultaneous contact between exposed- and/or extraneous-conductive-parts of the TT earthing system and exposed- and/or extraneous-conductive-parts of the TN-C-S (PME) earthing system of the main installation or any other earthing system of any other nearby installation.
gkenyon:
The issue we are discussing here is a little different - that of a TT supply separated from the network (specifically, the PME system). However, there are situations for EV charging installations where physical separation above and below ground cannot be achieved also.mapj1:However, I suspect that there won't be many 2m long insulating joints available for upgrading gas and water mains to current standards to permit TT and PME to co-exist, and I think that the idea that the earthing systems can always be separated in this way remains very optimistic.
I've seen one DNO that requires 3.5 m separation. Above ground at least, arm's reach (2.5 m) would be required by BS 7671.
My understanding is that metal gas and water mains, at least in the street, are being (or have been) replaced by plastic. Once this is completed, the place any remaining pipework (the bit up the driveway of a house, for example) is connected to the PME earthing system is in consumer's premises.
The situation may well be muddied by supply cables which have a conductive (or effectively conductive) earthed outer sheath.
But would it mean I can convert a whole installation to TT? Not always simple if an adjoining property is on PME. There are a number of situations where you might get caught out, e.g. two properties have roof-mounted TV antennas - the antenna systems may [should, but I know they aren't always] be earthed at one point, so if they are in arm's reach (or 3.5 m in one case) ...
"Providing a dedicated TT earthing system is only acceptable if there is no possibility of simultaneous contact between exposed- and/or extraneous-conductive-parts of the TT earthing system and exposed- and/or extraneous-conductive-parts of the TN-C-S (PME) earthing system of the main installation or any other earthing system of any other nearby installation.