Thinking a bit further - the hazard from a PME'd lamppost suffering from a broken CNE is often mitigated by the supplementary electrodes that DNOs (if not BS 7671) have been insisting be installed - and given the modest load can be reasonably successful at keeping touch voltages below hazardous levels.
and highlights the problems in the regs we do not really distinguish that cycle rack from a cast iron water main, and the both the Ze, and the chances of being bonded to the local PME CPC at an adjacent property are very different, and therefore so is the associated shock risk.
I think any form of words that really says 'don't bother if its just an isolated metal thing planted in or the ground' is reasonable.
However these will generally be encased in concrete. How should it be determined whether these are truely connected to Earth?