Bathroom zone
Former Community Member
i Have recently had my loft converted into a bedroom with an en-suite, my issue lays there is very little room in the en-suite and from the floor to the ceiling is 1.8m , will 230v IP rated downlights be okay in there? Or will these have to be 12v?
Don't forget 701.411.3.3. An R.C.D. is required for low Voltage circuits serving the location and also not serving the location but passing through Zones 1 and/or 2. (415.11).