fluke 1664fc tester

Hello. Does anyone have a fluke 1664fc tester, and have problems with it ? Most times I use it, it comes up with error message 5, which I think is interference on a circuit. Had the tester a couple of years now. Starting to wish a had bought a megger. It also trips rcds out, spoke to Fluke technical and their response was its a very complex tester, that's when technical is open, as apparently technical is closed on Tuesdays, as its the chaps day off !!!
Parents
  • Error code 5

    Excessive Noise

    Turn off all appliances (Loop, RCD measurements) or move the earth stakes (earth measurement).

    https://dam-assets.fluke.com/s3fs-public/166x____umeng0100.pdf


    So the same as the icon with a spike on a wave I am used to seeing on my Megger testers indicating a possibly less than accurate result due to installation conditions rather than a fault with the tester.


    It was trying to get reliable loop test results under less than perfect conditions on less than perfect installations that led me to buying a Megger two wire loop tester 

    https://uk.megger.com/2-wire-non-tripping-high-resolution-loop-testers-ltw425


    The downside of the dedicated two wire tester is it is slow, oh, so slow. Having said that it appears that the full test time for a lo-3 wire test on the Megger MFT1741 is three minutes 


    So having thought that when I bought my new MFT that can do lo-2 wire loop tests I would be getting rid of the dedicated no trip 2 wire tester, it looks like I will be keeping it.


    Regards the original post it looks like you will have to spend more time testing disconnecting loads and other circuits or try a different tester.


    Andy Betteridge 


Reply
  • Error code 5

    Excessive Noise

    Turn off all appliances (Loop, RCD measurements) or move the earth stakes (earth measurement).

    https://dam-assets.fluke.com/s3fs-public/166x____umeng0100.pdf


    So the same as the icon with a spike on a wave I am used to seeing on my Megger testers indicating a possibly less than accurate result due to installation conditions rather than a fault with the tester.


    It was trying to get reliable loop test results under less than perfect conditions on less than perfect installations that led me to buying a Megger two wire loop tester 

    https://uk.megger.com/2-wire-non-tripping-high-resolution-loop-testers-ltw425


    The downside of the dedicated two wire tester is it is slow, oh, so slow. Having said that it appears that the full test time for a lo-3 wire test on the Megger MFT1741 is three minutes 


    So having thought that when I bought my new MFT that can do lo-2 wire loop tests I would be getting rid of the dedicated no trip 2 wire tester, it looks like I will be keeping it.


    Regards the original post it looks like you will have to spend more time testing disconnecting loads and other circuits or try a different tester.