Max Zs BS7671 17th Edition / Guidance Note 3 Inspection and Testing

Former Community Member
Former Community Member
Hello,


There seems to be some slight differences with regards to acceptable Zs values when comparing the two documents BS7671 17th Edition A3 and Guidance Note 3 Inspection and Testing 17th Edition A3.


For example table 41.3 from BS7671 17th Edition A3 states:


0.4sec trip D6A = 1.82 Ω


Adjusted to 80% as per appendix 14 = 1.456 Ω



However page 121 from Guidance Note 3 Inspection and Testing 17th Edition A3 states:


0.4sec trip D6A = 1.46 Ω




These two documents are produced by IET. Guidance Note 3 Inspection and Testing 17th Edition A3 is rounding up Zs values above the maximum allowable values detailed in BS7671 17th Edition A3, why is that ?




ba51c8f3cf43a4eb3610fe4e2008860e-huge-20190722_083125.jpg


5d6415d8285e515a6e1d04f5ef5fb4b8-huge-20190722_083103.jpg






Parents
  • Former Community Member
    0 Former Community Member
    @mapj1

    Issue = IET contradictions in official documentations regards maximum allowable Zs values.


    measure Zs on  a real system = irrelevant to the above mentioned issue.


    measure values at different times of day = irrelevant to the above mentioned issue.


    meter accuracy = irrelevant to the above mentioned issue.


    meter lead resistance = irrelevant to the above mentioned issue.


    typical spec = irrelevant to the above mentioned issue.




    The contradiction may be deemed small and negligible and be explained away as such but at the end of the day it is still a contradiction.


    If the IET issue a document defining a value as the the maximum then they should not issue another document contradicting said document. 





Reply
  • Former Community Member
    0 Former Community Member
    @mapj1

    Issue = IET contradictions in official documentations regards maximum allowable Zs values.


    measure Zs on  a real system = irrelevant to the above mentioned issue.


    measure values at different times of day = irrelevant to the above mentioned issue.


    meter accuracy = irrelevant to the above mentioned issue.


    meter lead resistance = irrelevant to the above mentioned issue.


    typical spec = irrelevant to the above mentioned issue.




    The contradiction may be deemed small and negligible and be explained away as such but at the end of the day it is still a contradiction.


    If the IET issue a document defining a value as the the maximum then they should not issue another document contradicting said document. 