Mike M:
All digital Fluke and Megger loop impedance meters I have used are accurate enough to tell the difference between 1.45 Ω and 1.46 Ω .
Once again taking into account all that we know about tolerances and circuit variations, if something is defined as the maximum then surely it should it should never be acceptable to have a value higher than the maximum as far as the regs are concerned.
1.4566666667 Ω does not equal 1.46 Ω.
I beg to differ. The difference is less than nothing in that application,or if you prefer language with rather more mathematical rigour, it is less than the combination of instrumentation error and experimental variation and the results are statistically indistinguishable.
I suggest you go and measure Zs on a real system with a real meter early in the morning, then go out for lunch and polish the meter probes and re-test with the same meter at the same point in the afternoon. The two readings will be both as valid, but are unlikely to be the same in all digits. As an aside what meters do you suggest with this accuracy (not precision) ? Note that two half lengths of meter lead is a good few milli-ohms on its own. I have used both Fluke and Meggar machines and neither is this good.
A typical spec is more like this maker's data for the LTW 425 - and that is a dedicated loop tester, not a compromised design to make a multi function tester all fit in one box, they tend to be worse.
Loop Testing Accuracy |
±5% ±0.03Ω |
@230V a.c |
±10% ±0.02Ω |
To quote precision that is not there when recording results is actually wrong as it misleads the reader about the accuracy of the measurement.