gkenyon:
Neither of the methods you have discussed is 100 % accurate for an unbalanced system. In some installations, knowledge of the power factor of the loads on the phases (single-phase and three-phase) might also skew the answer.
The reason for this, is the actual voltage on the Neutral "shifts" in phase due to the imbalanced load.
gkenyon:
Neither of the methods you have discussed is 100 % accurate for an unbalanced system. In some installations, knowledge of the power factor of the loads on the phases (single-phase and three-phase) might also skew the answer.
The reason for this, is the actual voltage on the Neutral "shifts" in phase due to the imbalanced load.