gkenyon:
Neither of the methods you have discussed is 100 % accurate for an unbalanced system. In some installations, knowledge of the power factor of the loads on the phases (single-phase and three-phase) might also skew the answer.
The reason for this, is the actual voltage on the Neutral "shifts" in phase due to the imbalanced load.
gkenyon:
Now, if all that's too much, there is an easier way if you only want the worst-case volt-drop you could imagine, although this could potentially be a huge over-estimate.
(a) Take the largest line current for each phase you would envisage at the DB. Take the biggest one.
(b) Calculate the single-phase voltage drop. This will give you a larger result than the above calculation - an over-estimate, but very easy calculation.
(c) Calculate the three-phase voltage drop using this largest line current as the line current and assume it's balanced. This will give you the three-phase (line to line) voltage drop.
(d) Calculate the final circuit voltage drops from each of the circuits downstream, added to the relevant single-phase and three-phase values at the DB calculated in (b) and (c) respectively.
Farmboy:
Is this saying then that the total VD on, for example, L1 on an unbalanced 3ph distr cct with single ph final cct, is the single ph VD in the distr cct + the 3ph VD in the distr cct + the single ph VD of the final cct, all on L1?
Is there an example of calculating VD for unbalanced three ph system in the EIDG, i can't seem to see it?
Also, have they used the correct methodology in this article then? They seem to be calculating VD in the 3ph distribution cct for balanced and unbalanced systems, but don't make it explicit, yet use the 3ph mV for a balanced system. Sorry if I've misunderstood it.
professional-electrician.com/.../
F
Is there an example of calculating VD for unbalanced three ph system in the EIDG, i can't seem to see it?
Also, have they used the correct methodology in this article then? They seem to be calculating VD in the 3ph distribution cct for balanced and unbalanced systems, but don't make it explicit, yet use the 3ph mV for a balanced system. Sorry if I've misunderstood it.
professional-electrician.com/.../
gkenyon:
Sorry ... got diverted onto something else
Is there an example of calculating VD for unbalanced three ph system in the EIDG, i can't seem to see it?
No, page 65 para 2 explains why only a balanced option is used.
Also, have they used the correct methodology in this article then? They seem to be calculating VD in the 3ph distribution cct for balanced and unbalanced systems, but don't make it explicit, yet use the 3ph mV for a balanced system. Sorry if I've misunderstood it.
professional-electrician.com/.../
This follows the examples given in the EIDG - which assumes three-phase volt drop to the find DB and single-phase for the single-phase final circuit.
However, as I've said, if the system is so badly imbalanced (which may or may not cause other problems in the installation), then you can't really follow the broad guidance in the EIDG.