gkenyon:
Now, if all that's too much, there is an easier way if you only want the worst-case volt-drop you could imagine, although this could potentially be a huge over-estimate.
(a) Take the largest line current for each phase you would envisage at the DB. Take the biggest one.
(b) Calculate the single-phase voltage drop. This will give you a larger result than the above calculation - an over-estimate, but very easy calculation.
(c) Calculate the three-phase voltage drop using this largest line current as the line current and assume it's balanced. This will give you the three-phase (line to line) voltage drop.
(d) Calculate the final circuit voltage drops from each of the circuits downstream, added to the relevant single-phase and three-phase values at the DB calculated in (b) and (c) respectively.
gkenyon:
Now, if all that's too much, there is an easier way if you only want the worst-case volt-drop you could imagine, although this could potentially be a huge over-estimate.
(a) Take the largest line current for each phase you would envisage at the DB. Take the biggest one.
(b) Calculate the single-phase voltage drop. This will give you a larger result than the above calculation - an over-estimate, but very easy calculation.
(c) Calculate the three-phase voltage drop using this largest line current as the line current and assume it's balanced. This will give you the three-phase (line to line) voltage drop.
(d) Calculate the final circuit voltage drops from each of the circuits downstream, added to the relevant single-phase and three-phase values at the DB calculated in (b) and (c) respectively.