This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

What is the best way to wire ceiling lights?

The ceiling rose junction box with its loop-in wiring is now really showing its age and is no longer a practical (or even safe) installation for most residents who wish to install fancy light fittings. It is still, however, the most common arrangement for new build houses and rewires, probably as the result of the electrician's training and how they consider it to be the norm or they cannot think of (potentially better) alternatives.


So, what is the best way to wire ceiling lights? Should neutral wires be taken to the switches or not?
Parents

  • Dbat:

    Thats fine until a few years down the line when such records have been lost, and some poor electrician is struggling to fault find on a lighting circuit with only one cable at each light and switch. Then he's got to play russian roulette taking up carpets and boards to guess where this mystery central box you've installed is hidden under the floors. Any such box needs to be easy accessible and to easy to find. Even in a loft you'll be up and down the ladder alot disconnecting circuits to break down the fault, so whats the real benefit?




    If the records are kept in their proper place, which is within or adjacent to the DB (514.9.1), how do they get lost?


    And please somebody, tell me why a competently constructed installation should become faulty? ?

Reply

  • Dbat:

    Thats fine until a few years down the line when such records have been lost, and some poor electrician is struggling to fault find on a lighting circuit with only one cable at each light and switch. Then he's got to play russian roulette taking up carpets and boards to guess where this mystery central box you've installed is hidden under the floors. Any such box needs to be easy accessible and to easy to find. Even in a loft you'll be up and down the ladder alot disconnecting circuits to break down the fault, so whats the real benefit?




    If the records are kept in their proper place, which is within or adjacent to the DB (514.9.1), how do they get lost?


    And please somebody, tell me why a competently constructed installation should become faulty? ?

Children
No Data