Legh Richardson:
What sort of HiFi system requires 10 power supplies one wonders?
Pre-amp, power-amp, record player, cd player, tuner, both electrostatic speakers... I've guessed as far as 7 but yeah, no idea beyond that. Hi-fi is an industry full of magic and snake oil and you'll be surprised what audiophiles spend their cash on! EDIT: Some of it could be quite old too - 'vintage mojo' I believe it's called!
"The customer has now decided he doesn't want RCD anyway for 'reasons' " must be a qualified electrical engineer!
Legh
AJJewsbury:
I don't see how you can omit the 30mA RCD protection and claim either BS 7671 compliance or 'no less degree of safety' - without the RCD it lacks additional protection even if ADS is fine. A 100mA RCD isn't likely to be much better on that score either (no point in an 100mA RCD if 50mA can kill).
I agree. It would be deviation from the regulations once a 30ma RCD is omitted. I suppose it's shades of compliance...
If the inrush current is well beyond the RCD's current-carrying rating (e.g. 40A or 80A, not 30mA) then the L & N coils can saturate the torroid and combined with manufacturing tolerances can mean the L and N coils don't quite balance as they should and the sense coil sees an imbalance larger than it really is.
(or just let the user switch things on one at a time).
- Andy.
Maybe the RCD is serving its intended purpose.
A debatable solution is to remove the upfront RCD and replace it with as many BS8277 30mA RCD protected socket outlets as are required to spread the leakage or identify the actual problem.
The customer won’t like that, so the other solution is to walk away if you cannot identify a specific problem with the connected equipment.
Andy Betteridge
I liked the 'specially labelled socket for a specific piece of equipment' in the 17th AM3 because it makes sense in scenarios like this, particularly for those who work from home with a home workshop or multiple pieces of IT equipment.
A debatable solution is to remove the upfront RCD and replace it with as many BS8277 30mA RCD protected socket outlets as are required to spread the leakage or identify the actual problem.
AJJewsbury:
I liked the 'specially labelled socket for a specific piece of equipment' in the 17th AM3 because it makes sense in scenarios like this, particularly for those who work from home with a home workshop or multiple pieces of IT equipment.
But if the cluster of IT equipment was in danger of tripping a 30mA RCD in normal service then the leakage would have to be 15mA or above and then you're well into high protective conductor current territory and a BS 1363 socket is then verbotten.
A debatable solution is to remove the upfront RCD and replace it with as many BS8277 30mA RCD protected socket outlets as are required to spread the leakage or identify the actual problem.
Indeed debatable - as the 18th lists RCD types that are acceptable for additional protection - and BS 8277 isn't one of them. (Although there is a theory that that's just an oversight - I presume no-one's had any reassurance from the IET on that score yet?)
- Andy.
AJJewsbury:
I liked the 'specially labelled socket for a specific piece of equipment' in the 17th AM3 because it makes sense in scenarios like this, particularly for those who work from home with a home workshop or multiple pieces of IT equipment.
But if the cluster of IT equipment was in danger of tripping a 30mA RCD in normal service then the leakage would have to be 15mA or above and then you're well into high protective conductor current territory and a BS 1363 socket is then verbotten.
A debatable solution is to remove the upfront RCD and replace it with as many BS8277 30mA RCD protected socket outlets as are required to spread the leakage or identify the actual problem.
Indeed debatable - as the 18th lists RCD types that are acceptable for additional protection - and BS 8277 isn't one of them. (Although there is a theory that that's just an oversight - I presume no-one's had any reassurance from the IET on that score yet?)
- Andy.