Omitting 30ma RCD Protection for single S/O in a domestic property

Former Community Member
Former Community Member
I installed a dedicated circuit for a hifi system for a customer last year. The customer requested a 6mm2 radial from a 16A MCB housed in its own independent consumer unit into a single, un-switched socket outlet. No problem, bit unusual but no worries.I wired it using a 3c 6mm2 armoured cable as I half anticipated the forthcoming...


The hifi equipment is causing the rcd to trip when started up. I haven't been over to have a look but I am assuming that the startup current for the many power supplies (he has told me there are ten!) coupled with electronic earth leakage is causing a CPC current that is sufficient to trip the RCD (perhaps only 16ma but enough). The earthing is high integrity having a 6mm2 cpc + armour and the Zs is sufficiently low enough that the 16A MCB can be used for fault protection. So, if this wasn't domestic I'd ditch the RCD (or replace with a 100ma) assuming that my assumptions to this point are correct.


The customer has now decided he doesn't want RCD anyway for 'reasons' but I'm still wary of removing it in a domestic situation, not because I believe the installation would become less-safe but just because it contravenes regulations.


Assuming there's no fault on the equipment and it is just a case of startup/inrush current and earth leakage, what approach would you take? Remove the RCD and write it up as a deviation from 7671 with a signed disclaimer/waiver from the customer? Install a 100ma RCD? Do nothing and walk away? Something else?


Parents
  • Interesting situation. Can't use the HiFi system with the RCD in situ due to high start up currents causing high earth leakage. What sort of HiFi system requires 10 power supplies one wonders? unless its a test bench for assembling and testing disco type players with large PA ampifiers ie some form of commercial set up.

    I might start by running each power supply separately, with an oppropriate load, to see how much leakage current flowed. then? ..............

    Now " The customer has now decided he doesn't want RCD anyway for 'reasons' " must be a qualified electrical engineer!


    Legh
Reply
  • Interesting situation. Can't use the HiFi system with the RCD in situ due to high start up currents causing high earth leakage. What sort of HiFi system requires 10 power supplies one wonders? unless its a test bench for assembling and testing disco type players with large PA ampifiers ie some form of commercial set up.

    I might start by running each power supply separately, with an oppropriate load, to see how much leakage current flowed. then? ..............

    Now " The customer has now decided he doesn't want RCD anyway for 'reasons' " must be a qualified electrical engineer!


    Legh