Omitting 30ma RCD Protection for single S/O in a domestic property

Former Community Member
Former Community Member
I installed a dedicated circuit for a hifi system for a customer last year. The customer requested a 6mm2 radial from a 16A MCB housed in its own independent consumer unit into a single, un-switched socket outlet. No problem, bit unusual but no worries.I wired it using a 3c 6mm2 armoured cable as I half anticipated the forthcoming...


The hifi equipment is causing the rcd to trip when started up. I haven't been over to have a look but I am assuming that the startup current for the many power supplies (he has told me there are ten!) coupled with electronic earth leakage is causing a CPC current that is sufficient to trip the RCD (perhaps only 16ma but enough). The earthing is high integrity having a 6mm2 cpc + armour and the Zs is sufficiently low enough that the 16A MCB can be used for fault protection. So, if this wasn't domestic I'd ditch the RCD (or replace with a 100ma) assuming that my assumptions to this point are correct.


The customer has now decided he doesn't want RCD anyway for 'reasons' but I'm still wary of removing it in a domestic situation, not because I believe the installation would become less-safe but just because it contravenes regulations.


Assuming there's no fault on the equipment and it is just a case of startup/inrush current and earth leakage, what approach would you take? Remove the RCD and write it up as a deviation from 7671 with a signed disclaimer/waiver from the customer? Install a 100ma RCD? Do nothing and walk away? Something else?


Parents
  • Former Community Member
    0 Former Community Member

    Sparkingchip:
    Consumer unit suitable for one Hi-Fi or Home Cinema ring or spur


    Will a ring introduce more interference that can be detected by a HiFi purist than a radial?


    Given the apparent high leakage current is a ring a better option? Assuming distribution circuit being SWA with a core and the armour as a combined CPC already has earthing bigger than the live and neutral, which also screens it.


    Andy B.




     

    A ring will often act like a bloody big radiating antennae  - and SWA offers almost zero EMC screening at frequencies above mains frequency


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member

    Sparkingchip:
    Consumer unit suitable for one Hi-Fi or Home Cinema ring or spur


    Will a ring introduce more interference that can be detected by a HiFi purist than a radial?


    Given the apparent high leakage current is a ring a better option? Assuming distribution circuit being SWA with a core and the armour as a combined CPC already has earthing bigger than the live and neutral, which also screens it.


    Andy B.




     

    A ring will often act like a bloody big radiating antennae  - and SWA offers almost zero EMC screening at frequencies above mains frequency


    Regards


    OMS