mapj1:
That is interesting to know, thought it simply transfers the question to be asking if the EN standard 'arc' fault waveform actually represents the sort of current waveform you would get with a real fault of the kind you should disconnect.
This is very different to testing RCDs where we are all agreed that the test rig and the faults are similar, here I suspect there are real loads that look like arc faults, and arc faults that have signatures nothing like the standard test waveform.
With modern electronics it is possible to interrupt and reconnect in almost arbitrary speed and precision, so making an AFD tester that spits out a very complex set of test waveforms is a technically trivial matter - the hard work is agreeing what the waveforms should be.
I'm not sold on the idea myself, I thing we are some way from a useful item.
mapj1:
That is interesting to know, thought it simply transfers the question to be asking if the EN standard 'arc' fault waveform actually represents the sort of current waveform you would get with a real fault of the kind you should disconnect.
This is very different to testing RCDs where we are all agreed that the test rig and the faults are similar, here I suspect there are real loads that look like arc faults, and arc faults that have signatures nothing like the standard test waveform.
With modern electronics it is possible to interrupt and reconnect in almost arbitrary speed and precision, so making an AFD tester that spits out a very complex set of test waveforms is a technically trivial matter - the hard work is agreeing what the waveforms should be.
I'm not sold on the idea myself, I thing we are some way from a useful item.