arc
arcing
luminous discharge of electricity across an insulating medium, usually accompanied by the partial volatilization of the electrodes
Note 1 to entry: A complete sinusoidal current half-cycle is not considered to be an arcing half-cycle.
[SOURCE: IEC 62606:2013, 3.1]
and searching for "spark" includes the following:
(electric) spark
small luminous electric arc of short duration
whjohnson:
Just watched some chap on the E5 youtube channel visiting Eaton in Austria. Eaton AFDDs have been something of a subject of ridicule in youtubeland, with various respected electrical content providers demonstrating through various real-world means that they don't function. So, off this chap goes to Eaton's HQ in Vienna where they provide him with a aluminium case full of test kit, complete with the Eaton logo and fitted out with various Eaton devices inside.
One of the devices is the Eaton AFFDD which has famously failed to operate on numerous youtube video presentations.
Of course, it trips when tested with their own test kit. After all, no point in trying to sell something which isn't really needed unless you can demonstrate that it actually works, so Eaton helpfully provides the 'right' arc signature so that the device can trip on command in front of all those cynical doubters.
Apparently, all those heath robinson youtubers have been getting it wrong because they have unhelpfully been simulating real world arcing events which these devices won't actually pick up. You see, according to the 'experts' you need an arc instead of a spark to trip the device! What the hell is the difference?
Oh how I laughed! Is this how far they'll go to flog you some old tat you don't really need?
Just how many different arcs and sparks are there out there? Has anyone told David Attenborough of all these new species to explore?
Feel free to jump in!
mapj1:
That is interesting to know, thought it simply transfers the question to be asking if the EN standard 'arc' fault waveform actually represents the sort of current waveform you would get with a real fault of the kind you should disconnect.
This is very different to testing RCDs where we are all agreed that the test rig and the faults are similar, here I suspect there are real loads that look like arc faults, and arc faults that have signatures nothing like the standard test waveform.
With modern electronics it is possible to interrupt and reconnect in almost arbitrary speed and precision, so making an AFD tester that spits out a very complex set of test waveforms is a technically trivial matter - the hard work is agreeing what the waveforms should be.
I'm not sold on the idea myself, I thing we are some way from a useful item.