Erroneous test

Anyone know what this test is? It is listed in the same column  beside the insulation resistance tests on the installation test record sheet that needs to be completed by registered electrical contractors in Ireland.
Parents
    1. TAn internet search lead Here.



     4/15 - Test 6 - Erroneous connections

    The following test shall be carried out in order to detect erroneous connections between circuits: For each circuit, its protective device shall be switched off and an insulation test in accordance with Table 61A applied between phase conductors of that particular circuit and all other phase conductors.

    Note 1: This is an additional test to those specified in CENELEC HD 384.6.61:1992 Note 2: All loads in the circuit under test must be disconnected e.g. appliances switched off, lamps removed.


    Some years ago on this forum I referred to having completed such a test, as a test to ensure separation of circuits, but I was corrected, as over here testing for separation is taken to mean that you are testing to ensure that a SELV circuit is electrically separated across the transformer.


    Andy Betteridge
Reply
    1. TAn internet search lead Here.



     4/15 - Test 6 - Erroneous connections

    The following test shall be carried out in order to detect erroneous connections between circuits: For each circuit, its protective device shall be switched off and an insulation test in accordance with Table 61A applied between phase conductors of that particular circuit and all other phase conductors.

    Note 1: This is an additional test to those specified in CENELEC HD 384.6.61:1992 Note 2: All loads in the circuit under test must be disconnected e.g. appliances switched off, lamps removed.


    Some years ago on this forum I referred to having completed such a test, as a test to ensure separation of circuits, but I was corrected, as over here testing for separation is taken to mean that you are testing to ensure that a SELV circuit is electrically separated across the transformer.


    Andy Betteridge
Children
No Data