Sparkingchip:
Chris Pearson:
Sparkingchip:
Any circuit with junction boxes is a nightmare if fault finding has to be undertaken, there is rarely a reason why a domestic socket circuit should be wired through junction boxes from new.So how do you make a branch in a radial?
Ideally from the back of a socket.
"3 into 2 won't go."
Chris, what are you trying to say here? you lost me there
AJJewsbury:
"3 into 2 won't go."
Chris, what are you trying to say here? you lost me there
My answer to that is either to use brands that can take 12mm² (in practice many do) or shove some extra terminals into the back of the box
- Andy.
AJJewsbury:
"3 into 2 won't go."
Chris, what are you trying to say here? you lost me there
I think this is about BS 1363 accessories not necessarily being able to take 3off 4mm² conductors. My answer to that is either to use brands that can take 12mm² (in practice many do) or shove some extra terminals into the back of the box (not the neatest solution but being accessible, still preferble to a hidden JB somewhere, IMO).
All other sockets with 2 or 3 Ls and Ns are on the ring.
Zoomup:
AJJewsbury:
All other sockets with 2 or 3 Ls and Ns are on the ring.
But not a safe assumption when dealing with existing as earlier rulesWe professionals make no assumptions do we Andy? We would test for ring continuity.