Alcomax:
Yes, I'm still sticking with this one, because this piece of equipment may well be Class II, but supplies equipment which is not Class II, hence requires the cpc to each point in wiring on the way to the Class I equipment.
The regs in their current form can be read in a way that seems to recommend some highly suspect practice.
That's partly what I'm trying to illustrate. Let's be clear, I don't want to make a serious objection to the plastic REC2 isolator, and, if individual designers or installers believe that a plastic box with RCD meets the regs and is safe, then they should, of course follow their experience.
It's worth considering that, if BS 7671 (and its interpretation) were too prescriptive, some installations would not be practicable. I guess it's easier to be prescriptive in the tighter parameters of small houses, for example, but other installations need thinking "outside the box".
Alcomax:
From experience, the REC2 is not really suitable in most instances, but they are tried and tested. They are designed for their own isolator and that is fine.
Other makes exist, but Wylex is happy for their enclosure to be used for their Type S RCD - I have enquired of them.
Alcomax:
If you consider the tails to the consumers equipment in TT as a circuit- I assume you do from earlier comments- that circuit has double or re-inforced insulation as the "sole protective measure" [ dictated by 531.3.5.3.2.201] and 412.1.2 tells us, in general terms, this measure shall not be used to any circuit with an earthing contact. So you cannot have an earthing contact for termination.
don't forget, sheathed cables (e.g. T&E) are considered to have "double insulation".