Domestic SPD installation with a TNC-S earthing system.

Can a SPD be installed in a domestic installation without an earth conductor connecting it to the MET, because it will discharge the surge from the live line conductor to the neutral conductor?


Andy Betteridge
Parents

  • Without the earth connection the surge on the live has to discharge to the neutral through two surge devices in series,




    Only if they're wired CT1 - wire them CT2 and there's only one between L and N. It's probably easier though to go for a single two-terminal SPD and just connect it L-N anyway.




    does that work?



    If you did have two devices in a CT1 arrangement then it would sort of work, but the limiting voltage would be the sum of the two devices - so not ideal.


      - Andy.
Reply

  • Without the earth connection the surge on the live has to discharge to the neutral through two surge devices in series,




    Only if they're wired CT1 - wire them CT2 and there's only one between L and N. It's probably easier though to go for a single two-terminal SPD and just connect it L-N anyway.




    does that work?



    If you did have two devices in a CT1 arrangement then it would sort of work, but the limiting voltage would be the sum of the two devices - so not ideal.


      - Andy.