Without the earth connection the surge on the live has to discharge to the neutral through two surge devices in series,
Only if they're wired CT1 - wire them CT2 and there's only one between L and N. It's probably easier though to go for a single two-terminal SPD and just connect it L-N anyway.
does that work?
Hi all reading the calculations of the effect of wiring inductance how would an SPD work in a house with no N-E bond except one possibly out in the street? Seems like they wouldn't be terribly effective
AJJewsbury:
or one connected L-N and the other N-PE (CT2 - usually on TT but can also be used on TN). Sometimes two SPDs are packaged up together into single 3-terminal device - just to confuse matters.