Domestic SPD installation with a TNC-S earthing system.

Can a SPD be installed in a domestic installation without an earth conductor connecting it to the MET, because it will discharge the surge from the live line conductor to the neutral conductor?


Andy Betteridge
Parents

  • Hi all reading the calculations of the effect of wiring inductance how would an SPD work in a house with no N-E bond except one possibly out in the street? Seems like they wouldn't be terribly effective



    Indeed - which is why you'd normally need (at least) two. One connected L-PE and the other N-PE (CT1 - usually on TN systems) or one connected L-N and the other N-PE (CT2 - usually on TT but can also be used on TN).  Sometimes two SPDs are packaged up together into single 3-terminal device - just to confuse matters.


      - Andy.
Reply

  • Hi all reading the calculations of the effect of wiring inductance how would an SPD work in a house with no N-E bond except one possibly out in the street? Seems like they wouldn't be terribly effective



    Indeed - which is why you'd normally need (at least) two. One connected L-PE and the other N-PE (CT1 - usually on TN systems) or one connected L-N and the other N-PE (CT2 - usually on TT but can also be used on TN).  Sometimes two SPDs are packaged up together into single 3-terminal device - just to confuse matters.


      - Andy.