Eclipse:
Alan,
Thanks for that,
the incomng supply is tnc-s, so initially i was thinking of spliting the incoming tails through blocks and installing a single enclosed MCB which the SWA would terminate to, this then leaving the RCD at the shed end, correct or not?
if not, then as you suggest i'd have to try and retro fit an S type RCD into one side of the existing board.
Eclipse:
. . . the incomng supply is tnc-s, so initially i was thinking of spliting the incoming tails through blocks and installing a single enclosed MCB which the SWA would terminate to, this then leaving the RCD at the shed end, correct or not?
Alan Capon:
Eclipse:
. . . the incomng supply is tnc-s, so initially i was thinking of spliting the incoming tails through blocks and installing a single enclosed MCB which the SWA would terminate to, this then leaving the RCD at the shed end, correct or not?Correct. You don’t really need to protect the SWA with an RCD as long as you can operate the protective device from the far end in the event of a short to the armour. As John said, you need to insulate the armour and take just the phase and neutral into the consumer unit in the shed. The earth would then come from a local earth rod, ideally less than 200 ohms.
Regards,
Alan.